Rusell
July 8, 2025

Introduction

Recently, we came across a server power supply from xFusion. This unit supports 220–240V AC or 240V DC input, with an output voltage of 12.1V and an output current of 165.3A, delivering a total output power of 2000W. Under derated input conditions, the output power is automatically adjusted to 1000W or 1600W.

The input side features a cooling fan, power socket, and status indicator LED, while the output side uses a gold finger connector. Internally, the power supply adopts a PFC + LLC architecture and complies with the 80 PLUS Platinum efficiency standard.

Next, let’s take it apart to examine its internal components and structure.

Product Appearance

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The xFusion 2000W Platinum server power supply features a metal casing assembled with screws.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The nameplate is affixed on the front.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Model: PAC2000S12-1

AC Input: 200-240V; 50/60Hz; 10A

DC Input: 240V; 10A

DC Output: 12.1V; 165.3A Max

Maximum Total Output Power: 2000W Max

AC Input: 100-120V; 50/60Hz; 12A

DC Output: 12.1V; 83.3A Max

Maximum Total Output Power: 1000W Max

AC Input: 200-220V; 50/60Hz; 10A

DC Output: 12.1V; 133.3A Max

Maximum Total Output Power: 1600W Max

xFusion Digital Technology Co., Ltd.

Made in China

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

There are screws on the back to secure the internal PCBA module.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The sides are also secured with screws.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The input side has a handle, cooling fan, power indicator light, three-prong power socket, and a release latch.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The fan features an integrated guard labeled with conversion efficiency and output power.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Close-up of the three-prong power socket on the input side.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

There is a cutout corresponding to the cooling fan position to reduce the thickness.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The output side gold fingers are soldered with terminal posts.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The length of the module is about 205 mm (8.071 inches).

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The width is about 86.6 mm (3.41 inches).

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The thickness is about 39.5 mm (1.56 inches). 

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

That's how big it is in the hand.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The weight is about 1052 g (2.32 lb).

Teardown

Next, let's take it apart to see its internal components and structure.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Unscrew the screws and remove the top cover. Inside, there is a black insulating Mylar sheet.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The PCBA module is secured inside the enclosure with screws.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Remove the PCBA module; inside the enclosure, there is a white insulating Mylar sheet.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The PCBA module is composed of multiple small PCBs soldered together, and the fan wiring is insulated with heat shrink tubing.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The fan is connected via a plug connector.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The cooling fan is from Delta, model FFB0412EN-00, rated at 12V 2.1A, made in China, and equipped with static blades.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

On the front side of the PCBA module, the AC input section is located at the lower left corner. It includes components such as fuses, safety X2 capacitors, varistors, common mode chokes, and bridge rectifiers. Adjacent to this area on the right are PFC boost inductors, with heatsinks mounted below that secure the PFC MOSFETs and rectifiers. At the bottom, there are high-voltage filter capacitors.

To the right, there are symmetrical LLC power modules, each on a small PCBs that contain MOSFETs, transformers, synchronous rectifiers, and filter capacitors. Below these modules on the right side are control PCBs and auxiliary power supply modules. The high-voltage filter capacitors at the bottom are insulated by heat-shrinkable tubing and are fixed in place with adhesive.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

On the back side, there are PFC controllers, synchronous buck chips, and drivers. On the left side of the output, there are synchronous buck chips, op-amps, ideal diode controllers, synchronous buck converters, and power control transistors.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The individual small PCBs are separated. Observing the PCBA module reveals that it uses a boost PFC combined with dual LLC power stages for output, all controlled by TI controllers. ADI drivers drive the PFC MOSFETs and synchronous rectifiers, while the LLC MOSFETs use ADI isolated drivers.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

At the input side, there are power sockets, fuses, safety X2 capacitors, a varistor, a common mode choke, and bridge rectifiers.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Two fuses at the input side are insulated with heat-shrink tubing.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Rated at 15A.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The safety X2 capacitor is from Faratronic. 1.5μF. 

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The varistor is from FNR, model FNR-14K621, used to absorb overvoltage surges.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The common mode choke is wound with a magnetic ring, and it's also insulated with bakelite. 

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The other safety X2 capacitor is rated at 0.33μF.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The two blue Y capacitors come from Walsin.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

On the side of the PCBA module, there is a bridge rectifier, a PFC boost inductor, a resonant inductor, and an LLC transformer.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The bridge rectifier is secured to the heatsink.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The bridge rectifier is from LRC, model D25SB80, rated at 800V 25A, and uses a D5 package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The film filter capacitor is from Faratronic. 1.5μF 450V. 

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The PFC controller is from TI, model TMS320F28022. The chip features a built-in C2000 32-bit MCU with a main frequency of 50MHz, 32KB of flash memory, and 12KB of SRAM. It supports UART, SPI, and I2C interfaces and comes in an LQFP48 package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The PFC MOSFET driver is from ADI, marked with 78, model ADP3654. It is a high-speed dual-channel 4A driver featuring an industrial-standard compatible pin layout and high current driving capability. The driver comes in an MSOP8EP package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The op-amp is from ADI, marked with ABAA, model MAX4239AUT. It is an ultra-low offset, low-noise, high-precision op-amp packaged in SOT23.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The inverter is from Nexperia, marked with "V04," model 74LVC1G04GV, and comes in an SOT753 package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The synchronous buck chip is from MPS, model MPQ28261. It is a synchronous buck converter with 21A input and 3A output current. The chip integrates MOSFETs internally, operates at a switching frequency of 500kHz, and comes in a QFN14 package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Close-up of the 10μH buck inductor.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The PFC MOSFET and PFC rectifier are mounted on the heatsink.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The back of the heatsink is slotted to enhance heat dissipation.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The PFC MOSFET is from Infineon, marked with 6R041C6, model IPW60R041C6. It is an NMOS with a voltage rating of 650V and an on-resistance of 41mΩ, packaged in TO-247.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The SiC diode is from RePower, model NXPSC10650, rated at 650V 10A, and packaged in TO-220-2L.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Two 20mΩ resistors are connected in parallel to sense the current of the PFC MOSFET.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Close-up of the PFC inductor core.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The PFC inductor is wound with flat copper wires, and it's also insulated with bakelite.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

There are high-voltage filter capacitors on this side.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The high-voltage filter capacitors are soldered onto a small PCB.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

There are no components on the back.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The high-voltage filter capacitor is from NCC, rated at 450V 680μF.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The other two electrolytic capacitors are from Nichicon, each rated at 68μF 450V.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

A filter capacitor of the same model is also soldered on another small PCB.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

There is a thermistor and a relay on this small PCB.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The relay is from HONGFA, model HF32F/012-HSLQ. It is an ultra-compact medium-power relay with a single normally open contact, rated at 8A 250V, and operates at a coil voltage of 12V.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The blue thermistor is from TDK, with adhesive applied at the bottom for reinforcement.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

On one side of the auxiliary power PCB, there is a primary master control chip, a planar transformer, and a rectifier.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

On the other side, there is a feedback optocoupler and diodes.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The primary master control chip is from Infineon, model ICE2QR2280G. It integrates an 800V MOSFET and supports 30W output power under wide voltage input. The chip comes in a DSO-12 package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Close-up of the planar transformer.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The feedback optocoupler is from Everlight, model EL3H7, used for output voltage feedback.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The ultrafast diode on the left is from VISHAY, marked with UK, model US1K, rated at 800V 1A, and packaged in SMA. The TVS on the right is also from VISHAY, marked with 170A, model P6SMB170A, with a working voltage of 145V, and packaged in SMB.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The ultrafast recovery diode is from VISHAY, marked with "MD," model MURS120-M3, rated at 200V 1A, and packaged in SMC.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

This ultrafast recovery diode is from DIODES, model PDU620, rated at 200V 6A, and packaged in PowerDI5.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The other diode has the same model number.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The front side of the LLC control PCB has a controller, a connector socket, and communication optocouplers.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The back side has op-amps, a memory chip, and communication optocouplers.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The LLC controller is from TI, marked with TMS320 980 SPC032PAGT. It is used for half-bridge LLC control and synchronous rectification control, and comes in an LQFP64 package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The memory chip is from STMicro, model M24C64-W, with a capacity of 8KB, and packaged in SO8.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The dual op-amp is from TI, model TLC2272A. It is a dual-channel, low-noise, rail-to-rail operational amplifier, and comes in an SOIC-8 package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The other dual op-amp is the same model.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Three Everlight EL1018 optocouplers are used for communication isolation.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Close-up of the other two optocouplers.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The two filter capacitors have a rating of 100μF 16V.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The inverter is from Nexperia, model 74LVC1G04GV.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

There are two LLC modules on the output side.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The front side of the LLC module is soldered with resonant capacitors and a transformer, while the right side is soldered with output filter capacitors.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The back side is soldered with LLC MOSFETs, resonant capacitors, diodes, an isolation driver, synchronous rectifiers, and current sense resistors.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The isolation driver is from ADI, model ADUM4223. It is an isolated precision half-bridge driver with a 4A output current and 5kV RMS isolation capability, packaged in SOIC-1.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The LLC MOSFETs are from Infineon, marked with 65F6165, model IPL65R165CFD. They are NMOS devices with a voltage rating of 700V, an on-resistance of 165mΩ, and come in VSON-4 packages.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Close-up of a set of NPO resonant capacitors.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

There is also a set of NPO resonant capacitors on the other side.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Two series-connected diodes are from Onsemi, model MURHD560W1T4G. They are ultrafast recovery diodes rated at 5A 600V and packaged in DPAK.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The transformer primary winding is made with Litz wire, while the secondary winding is formed by soldered copper strips.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The synchronous rectifier driver uses the ADI ADP3654.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The synchronous rectifiers are from Onsemi, model NTMFS5C612NL. These are NMOS devices rated at 60V with an on-resistance of 1.5mΩ, and come in DFN5 packages.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The other two synchronous rectifiers are of the same model.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

In addition, there are two more synchronous rectifiers of the same model.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The rectifiers are grouped in sets of three for LLC synchronous rectification, helping to distribute heat evenly and reduce temperature rise.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The output filter capacitors are from Panasonic, part of the SVPG series of conductive polymer solid capacitors. They are rated at 270μF 16V, with three connected in parallel.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Two 0.5mΩ resistors are connected in parallel to sense the output current.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The other LLC PCB is symmetrically designed to the previous one, with only the four output filter capacitors being different.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The backside layout is identical, so it will not be described further to save space.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The filter capacitors are rated at 270μF 16V.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The LLC resonant inductor is wound with Litz wire.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

This output filter capacitor is rated at 1200μF 16V.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The other output filter capacitor is rated at 270μF 16V.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The output VBUS MOSFET is from VISHAY, model SiRA20DP. It is an NMOS device rated at 25V with an on-resistance of 0.48mΩ, packaged in PowerPAK SO-8.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The backside also has two VBUS MOSFETs of the same model.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The dual op-amp is from ADI, model AD823. It is a high-precision dual-channel op-amp with rail-to-rail JFET inputs, supports single-supply operation, and comes in an SOIC-8 package.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The ideal diode controller is from TI, model LM5051. It is designed for low-side applications, supports input voltages down to 100V, features a built-in NMOS driver, offers a fast reverse response time of 50ns, and is packaged in an SOIC-8 case.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The MPQ28261 synchronous buck converter is used to supply power to the control PCB.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Close-up of the 10μH buck inductor.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

The thermistor is used to monitor the temperature at the power supply air inlet.

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Well, those are all components of the xFusion’s FusionWatt 2000W Platinum Server Power Supply.

Summary of ChargerLAB

Teardown of xFusion’s FusionWatt 2000W Platinum Server Power Supply-Chargerlab

Here is the component list of the xFusion’s FusionWatt 2000W Platinum Server Power Supply for your convenience.

Model PAC2000S12-1, supporting a wide input voltage range with a rated output power of 2000W. It features an internal cooling fan that draws air in from the output side and exhausts it through the input side for heat dissipation.

After taking it apart, we found that it uses a PFC+LLC architecture. The PFC controller is a TI TMS320F28022 paired with an ADI ADP3654 driver, utilizing Infineon IPW60R041C6 MOSFETs and RePower NXPSC10650 SiC diodes.

The LLC controller uses the SPC032PAGT. The power stage features a symmetrical dual-channel design, with primary MOSFETs being Infineon IPL65R165CFD devices, driven by ADI ADUM4223. The synchronous rectifiers are Onsemi NTMFS5C612NL. The auxiliary power supply uses the Infineon ICE2QR2280. All internal capacitors are Japanese-brand, and the output is filtered with solid capacitors, reflecting solid and reliable workmanship and material quality.

Related Articles:
1. Teardown of CUKTECH 10 GaN Charger Ultra (AD1204U)
2. Teardown of Lenovo thinkplus FLUXO 140W 20000mAh Power Bank (SLPB-20140)
3. Teardown of DJI 2600W 1024Wh Power 1000 V2 Portable Power Station

2000W xFusion
3
ChargerLAB POWER-Z ET240 PD Protocol Analyzer User Guide: DisplayPort Alt Mode and AUX Analysis
Previous
Teardown of Huawei WATCH 2nd-Gen Wireless SuperCharger (CW05)
Next

Hot posts

Teardown of VERTIV 3500W SiC Rectifier Module (R48-3500e3)
Teardown of EcoFlow 240W USB4 Fast Charging Braided Cable (Video)
Teardown of EcoFlow 240W USB4 Fast Charging Braided Cable
Charging Compatibility Test of MIIIW 140W GaN Charger (Xiaomi Phones)

Related posts

Teardown of UUGreenPower UR100020‑SW 20 kW Ultra‑Wide Voltage Constant Power Charging Module

Teardown of UUGreenPower UR100020‑SW 20 kW Ultra‑Wide Voltage Constant Power Charging Module

October 13, 2025
0
Teardown of Bel Fuse 3000W GaN Server Power Supply (TET3000-12-069RA)

Teardown of Bel Fuse 3000W GaN Server Power Supply (TET3000-12-069RA)

October 10, 2025
0
Teardown of Gospower 1300W DC Server Power Supply (G1232-1300WND)

Teardown of Gospower 1300W DC Server Power Supply (G1232-1300WND)

October 9, 2025
0
Teardown of 372W Power Supply (For SONY PlayStation 5)

Teardown of 372W Power Supply (For SONY PlayStation 5)

February 28, 2022
4
3

ABOUT ME

As a sibling site of chongdiantou.com, ChargerLAB covers everything about charging, including chargers, wireless chargers, power banks, cables, car chargers, portable power stations and other peripherals. You can contact us by sending the email to info@chargerlab.com.

FOLLOW US

Facebook Instagram TikTok Twitter YouTube

E-COOL MEDIA

POWER-Z Chongdiantou 52Audio
Copyright © 2016-2026 Chargerlab. Designed by nicetheme.
  • News
    • What's New
    • Interviews
    • Vlogs
    • Events
    • Industry
  • Reviews
    • Charging Compatibility
    • Fully Charging
    • Comparison
    • Chargers & Cables
    • Power Banks & Stations
    • Mobile Devices
    • Accessories
  • Teardowns
    • Chargers & Cables
    • Power Banks & Stations
    • Power Supplies
    • Prototypes
    • Batteries
    • Accessories
  • Videos
    • YouTube
    • TikTok
  • Guides
    • How to Buy
    • Explained
    • Deals
    • ICs
  • POWER-Z
    • KM003C/KM002C
    • KT002
    • Buy POWER-Z
    • Technical Support
  • Contact Us
  • Apple
  • GaN
  • ANKER
  • Power Bank
  • 100W
  • 65W
  • ChargerLAB
  • Xiaomi
  • Baseus
  • iPhone 15

Rusell

Editor